Vess R2600ti. Uninterruptible power supply

  • 32 Views
  • Last Post 4 hours ago
doctor38 doctor38 posted this 2 days ago

 

Hello. I have a Vess R2600ti. Not long ago I reconnected to a new UPS (uninterruptible power supply). I have 3 power supplies. I decided to connect the power supplies to different UPSs, so that if one backup power source fails, the system will work on the second one. But the problem is that when I started checking this circuit, my vess beeped but did not start, although I thought that it would work on one power supply and report that the second one did not work.

Maybe I'm wrong. Write how the system should work if one power supply fails. The screenshot shows how I connected it to the backup power supply.And one more question: I have 3 power supplies (this can be seen from the screenshot) Which one is the backup power supply? If which power supplies fail, will the system shut down?

Attached Files

Order By: Standard | Latest | Votes
doctor38 doctor38 posted this 2 days ago

R P posted this 4 hours ago

Hi,

The Vess R2600 uses what's called N+1 redundant power supplies. That means that N supplies are needed for the Vess to run and any power supply can fail or be offline and operation will continue. All three power supplies are connected to the power bus, two are needed for the Vess to operate normally. There is no power supply that is a dedicated backup.

From the look of it, connection 1 should work. Connection 2 will only power 1 power supply, which is not enough.

Probably it would be best to connect all three power supplies to one UPS.